Jump to content
LIMITED TIME OFFER: Get up to $100 off tuition for Master Samurai Tech courses through November 30th ×
Click here to check out this guide

FAQs | Repair Videos | Academy | Newsletter | Contact


DISCLOSURE: We may earn a commission when you use one of our coupons/links to make a purchase.
  • Upcoming Events

    • 07 December 2024 03:00 PM Until 04:00 PM
      0  
      All Appliantology tech members are invited to join in the conversation for all things Appliantological: bidness, customers, tools, troubleshooting, flavorite brewski, whatever. Webcams and microphones are open and live!
      This event is also a great time for any students at Master Samurai Tech to bring any and all questions about the coursework. We're happy to walk through any concepts you're having trouble with. Think of it like office hours with your teachers. 
      Also, follow this Calendar Event so you'll get notified of new posts here. Look for the "Follow" button either at the top of the topic on desktop or below the topic on mobile.
      Who: This workshop is only available to tech members at Appliantology.
      When: Saturday, December 7 @10:00 AM Eastern Time.
      Where: Online via Zoom
      How:
      Click here to go to the forum topic with the registration link. If you're interested, register now. Arrive a couple minutes early to make sure your connection is working. Set a reminder for yourself for this workshop so you don’t miss it.  And check out past workshops here: https://appliantology.org/announcement/33-webinar-recordings-index-page/

Recommended Posts

Posted

I have a York Diamond 80 heater blowing cold air. The unit is ~22 years old with no issues until now. Initial troubleshooting found the 120 Vac hot wire had pulled out of the wire nut and shorted to the metal case. I repaired that which allowed fans to come on but still no hot air. Thermostat seems to work ok with heater (turning on aux fan) and fan control (which turns on main fan but no heat). Pretty sure gas is working at least to the heater unit since kitchen cooktop burners work fine and I smelled slight gas during one trip to the attic near the furnace. Glow bar turns on and smaller fan comes on but no gas burners and then the glow bar turns back off after ~30 seconds or so. Tried resetting all 3 rollout switches and tried turning gas valve off and then back on. But still no hot air. Gas valve is getting ~28 Vac while glow bar is on but then turns off when glow bar goes off. Measured the resistance across the input to the gas valve and it reads open. So I assume this means the gas valve solenoid is dead. I checked control board diagnostic LED and it goes red when the unit first turns on but is not lit at all after that (no blinking codes). Can just the solenoid be replaced or does the entire gas valve need to be replaced? Anything else I should try before purchasing a gas valve? Thanks for your help.

  • Replies 5
  • Created
  • Last Reply

Top Posters In This Topic

  • 16345Ed

    2

  • RMN

    2

  • spencertech

    1

  • Gags730

    1

Top Posters In This Topic

Posted (edited)

I know next to nothing about furnaces. But sounds like classic ignitor failure. 

Edited by 16345Ed
Posted

check for 24v to gas valve after igniter warm up but it seems like you have to replace the gas valve

Posted

Thanks for the suggestions. Ignitor seems to work since glow bar gets red hot but nothing ignites so I'm assuming that the gas valve is the cause. It has ~24V across it while the glow bar is on but that then goes away after nothing ignites. I also measured an open resistance across the gas valve solenoid so I assume that also means it is bad. Just wanted to make sure that was it and I wasn't missing checking something else before I bought a replacement.

Posted (edited)

I missed part about no resistance on valve. 

 

However ignitors can and do fail yet still glow. 

Edited by 16345Ed
Posted

Check for 24 Volts at the Valve. 

If you have the voltage at the valve then Kill the power, and you need to check for continuity across the valve.  With the wires pulled  off the valve,  You should have continuity.  If not replace the valve.