Jump to content
Click here to check out this guide

FAQs | Repair Videos | Academy | Newsletter | Contact


DISCLOSURE: We may earn a commission when you use one of our coupons/links to make a purchase.
  • Upcoming Events

    • 10 May 2025 02:00 PM Until 03:00 PM
      1  
      All are invited to join in the conversation for all things Appliantological: bidness, customers, tools, troubleshooting, flavorite brewski, whatever. Webcams and microphones are open and live!
      Also, follow this Calendar Event so you'll get notified of new posts here. Look for the "Follow" button either at the top of the topic on desktop or below the topic on mobile.
      Who: This workshop is available to everybody, including you! You don't have to be a member of Appliantology to join the fun.
      When: Saturday, May10 @10:00 AM Eastern Time.
      Where: Online via Zoom
      How:
      Click here to register. If you're interested, register now. Arrive a couple minutes early to make sure your connection is working. Set a reminder for yourself for this workshop so you don’t miss it. 

Fixing my AC Split syst.


rbravo46

Recommended Posts

Posted

My AC 3 ton split syst. is not cooling right. The low presure side is 70 psi. & high

presure side is 250 psi. with 88 F. ambient temp. The Compresor is consuming

8 A. instead 13 A. The return pipe on Compresor is swething & the Evaporator is

working just at 25% of his capacity.    I have replaced the Blower but still no change.

What could be causing this problem ?    Thank for any help,:huh:

 

 

  • Replies 4
  • Created
  • Last Reply
Posted

Low side high, high side low, not pulling rated amps. Inefficient compressor.

Posted

have you cleaned the outside unit?

 

  • 2 weeks later...
Posted

[user=10647]rbravo46[/user] wrote:

My AC 3 ton split syst. is not cooling right. The low presure side is 70 psi. & high

presure side is 250 psi. with 88 F. ambient temp. The Compresor is consuming

8 A. instead 13 A. The return pipe on Compresor is swething & the Evaporator is

working just at 25% of his capacity. I have replaced the Blower but still no change.

What could be causing this problem ? Thank for any help,:huh:

Reply: That's a lot of difference in current. Like it's not doing much work at all. Take the actual temperature of the return line at the condenser input with a service thermometer and compare it to the guages pressure/temp readings. The difference should be less than 10 degrees and five is prefereable. If not - add freon.

Posted

why did you replace the blower? If you replaced the blower did you replace it with the same speed blower or opt for more speed?

 if you did you messed up

 