Jump to content
LIMITED TIME OFFER: Get up to $100 off tuition for Master Samurai Tech courses through November 30th ×
Click here to check out this guide.

FAQs | Repair Videos | Academy | Newsletter | Contact


DISCLOSURE: We may earn a commission when you use one of our coupons/links to make a purchase.
  • Upcoming Events

    • 07 December 2024 03:00 PM Until 04:00 PM
      0  
      All Appliantology tech members are invited to join in the conversation for all things Appliantological: bidness, customers, tools, troubleshooting, flavorite brewski, whatever. Webcams and microphones are open and live!
      This event is also a great time for any students at Master Samurai Tech to bring any and all questions about the coursework. We're happy to walk through any concepts you're having trouble with. Think of it like office hours with your teachers. 
      Also, follow this Calendar Event so you'll get notified of new posts here. Look for the "Follow" button either at the top of the topic on desktop or below the topic on mobile.
      Who: This workshop is only available to tech members at Appliantology.
      When: Saturday, December 7 @10:00 AM Eastern Time.
      Where: Online via Zoom
      How:
      Click here to go to the forum topic with the registration link. If you're interested, register now. Arrive a couple minutes early to make sure your connection is working. Set a reminder for yourself for this workshop so you don’t miss it.  And check out past workshops here: https://appliantology.org/announcement/33-webinar-recordings-index-page/

Recommended Posts

Posted

I'm hoping that I can get some advice for my central A/C unit in my home. I've climbed up in the attic and removed the side cover for the coils, it's clean and clear, my filter is in the ceiling and was clean, but I replaced anyway. The outside coils have been cleaned ad have good flow through the coils. After the unit has been on for about 30 min. it ices up from inside coils down to the outside coils. The outside coils don't ice but the line leading from there to inside coils do. The inside coils ice over so bad the fan can't push air through coils, I have to shut unit down and set fan on manual to defrost coils. Is there a relay or switch that may have expired, or has my pump failed...? 

At a loss...

Thanks,

Woody

  • Replies 4
  • Created
  • Last Reply

Top Posters In This Topic

  • Woody

    3

  • ECtoFix

    1

  • HVAC_Jimbo

    1

Posted
3 hours ago, Woody said:

I've climbed up in the attic and removed the side cover for the coils, it's clean and clear, my filter is in the ceiling and was clean, but I replaced anyway.

That’s good.  Airflow is key.  Just be sure you’re using a standard pleated air filter, which should be replaced monthly.   Some of those fancy & expensive “micron” filters will affect proper air flow and shouldn't be used unless prescribe by the manufacturer.

3 hours ago, Woody said:

The outside coils have been cleaned ad have good flow through the coils.

The outside coils eject heat brought from the conditioned space (your house). That coil should be HOT (above 90°F-ish).

FYI: If airflow through the outside coils get restricted (clogged), this will NOT cause a freeze-up, but will INDEED affect overall system performance.

3 hours ago, Woody said:

After the unit has been on for about 30 min. it ices up from inside coils down to the outside coils. The outside coils don't ice but the line leading from there to inside coils do.

The outside coils won’t ice up, but the low pressure suction line to the compressor might ice up if the indoor coil isn’t absorbing the heat load as it should.

3 hours ago, Woody said:

The inside coils ice over so bad the fan can't push air through coils, I have to shut unit down and set fan on manual to defrost coils.

The question here would be whether the inside coil has enough airflow across it.  You said it’s clean, and the filter is NEW…so you’ve done all that’s expected by a prudent homeowner.

3 hours ago, Woody said:

Is there a relay or switch that may have expired, or has my pump failed...? 

By saying the pump, you mean the compressor.  A faulty compressor does NOT cause a freeze-up.  Actually, it would do the opposite by NOT cooling down to the temperature expected in a properly functioning system.

 Also, no relays or switches will cause that either…unless somehow one of them is diminishing proper fan motor speed (airflow)....which CAN cause a freeze-up.

*     *     *     *     *     *     *     *     *     *     *     *     *     *     *     *     *     *     *     *

Air-conditioners freeze up for one of three reasons:

  • Low indoor airflow, which can be caused by several things (some of which you'd addressed)

  • A low refrigerant charge - due to a leak somewhere in the system

  • A refrigerant restriction, which can be several places within the system

You've done everything expected as a homeowner.  It's time to call a HVAC company to address your issue.

 

Posted

Thank you for responding...! Out of all of your advise, the one thing that stands out for me, is that I've been using a higher grade intake filter. A Honeywell #7, not the top of the line#9, not the bottom#4. I'll try running it with no filter and see if I have the issue, then if it persists, like you said HVAC call time.

Thank You Again!!

😎🥶

Posted

Had to make the call for help....

  • 5 weeks later...
Posted

Low on charge, TXV issue possible. Unless your a HVAC Tech make the call.