Jump to content
Click here to check out this guide

FAQs | Repair Videos | Academy | Newsletter | Contact


DISCLOSURE: We may earn a commission when you use one of our coupons/links to make a purchase.
  • Upcoming Events

    • 07 June 2025 02:00 PM Until 03:00 PM
      1  
      All are invited to join in the conversation for all things Appliantological: bidness, customers, tools, troubleshooting, flavorite brewski, whatever. Webcams and microphones are open and live!
      Also, follow this Calendar Event so you'll get notified of new posts here. Look for the "Follow" button either at the top of the topic on desktop or below the topic on mobile.
      Who: This workshop is available to everybody, including you! You don't have to be a member of Appliantology to join the fun.
      When: Saturday, June 7 @10:00 AM Eastern Time.
      Where: Online via Zoom
      How:
      Click here to register. If you're interested, register now. Arrive a couple minutes early to make sure your connection is working. Set a reminder for yourself for this workshop so you don’t miss it. 

Recommended Posts

Posted

Haven't posted for some years so hope I'm asking for help in the right forum.  I did an old  Maytag washer stem and seal replace with Appliantology's help  some years ago.  My carrier central AC 38CKC030-301 compressor isn't engaging.  When it's working I can hear the gas running through the copper tube to the drying filter to my condenser in the plenum.  Not a sound now and outside only the cooling fan is running.  Don't hear the compressor running at all.  I'm told  I can check some small parts like a relay for capacitor.   Can anyone confirm this or refer me to a manual for troubleshooting?

Thanks so much,

Frank

  • Replies 2
  • Created
  • Last Reply

Top Posters In This Topic

  • romanof

    2

  • MrappliancesChandler

    1

Top Posters In This Topic

MrappliancesChandler
Posted

The contactor turns the compressor on. Get a cap tester, they're cheap.

Next step would be to ohm out the compressor and check wiring at compressor

to make sure the terminals are sound.

Posted

MrappliancesChandler,

Fortunately I'm one of those guys who has some basic electrical testing tools but didn't need one.  Found one connection shorted on the DP contactor.  I tried to order through Repair Clinic but those guys were out of stock for two weeks.  So.  Found a local supplier who had one.  I replaced the motor run capacitor too since the OHM readings across common to fan or herm side were strange.  Reading goes up but not down like it should according to what I've been told.

Anyway.  Thanks for the input.  I'll always get the help I need from you guys.